System Sensor 200 series
1993
System Sensor 500 series |
System Sensor FAAST series |
"title": "200 series",
The System Sensor 200 series is a series of addressable detectors.
The 200 series was released in 1993 as a low-profile version of the 500 series with common housing for ionization and photoelectric smoke detectors.[1]
In 1995, System Sensor introduced the 3251 OMNI Sensor with ionization, photoelectric, and heat sensors.[2] The OMNI Sensor featured thermistors similar to the 2300 series, but the thermistor cells were reduced in size to match the 1251 and 2251.
Around 2000, the 1251 and 2251 were updated to place the digits on the address switches closer together, providing space for options 10-15 on advanced protocol models. The 5251P and 5251RP heat detectors were also introduced as successors to the 5551B and 5551R with this change, and the 2251T was introduced with a similar thermistor design to the 3251 to replace the 2551THR.
In late 2000, System Sensor introduced the 2251TM Acclimate detector.[3][4] The OMNI Sensor was later discontinued and replaced with the Acclimate detector.[5]
In 2002, System Sensor introduced the Pinnacle laser smoke detector as a replacement for the LZR-1.[6]
In 2003, all detectors besides the Pinnacle detector were redesigned to have a shape more closely resembling the i3 series.[7] The new models could be identified with the "B" suffix, and the standard temperature heat detectors were marked with a gray circle outline. The 5251H was also introduced at this time, featuring the new design and a black circle marking.
Between 2003 and 2004, the duct detectors were updated to support a wider air velocity range. The new models had an L suffix at the end.
In 2004, beam detectors were introduced.[8] These were similar to the conventional beam detectors in the BEAM series.
In 2007, System Sensor introduced the 2251-COPTIR, which included 4 sensors.[9][10] System Sensor also introduced the 7251DH laser duct detector around this time.[11]
Around 2008, the B224RB relay base and B224BI isolator base were redesigned to resemble the B200S sounder base, which was released in 2009 together with the B200SR.[12][13] The B200SR functioned as a replacement for the B501 sounder bases, while the B200S was controlled by the FACP. Both models used the same tone as the SpectrAlert Advance horn.
Between 2009 and 2010, System Sensor discontinued the Innovair detectors due to the release of the InnovairFlex series.[14] The 2251BR was released as a remote test capable detector that could be placed in an InnovairFlex base.
In 2015, System Sensor introduced the B200S-LF and B200SR-LF as low frequency versions of the B200S and B200SR respectively.[15]
In July 2015, System Sensor discontinued the ionization smoke detectors due to the increased manufacturing and recycling costs.[16] Depending on the application, consumers were instructed to use photoelectric, multi-criteria, aspirating, or laser detectors.
| Model | Protocol | Replaced | Replaced by |
| 1251[17] | CLIP | 1551B | 1251B |
| 1251B[18] | 1251 | 2251B 2251TMB 2251-COPTIR 7251 8251F |
| Model | Protocol | Heat sensor? | Intrinsically safe? | Remote test capable? | Replaced | Replaced by |
| 2251 | CLIP | No | No | No | 2551HR | 2251B |
| 2251T | CLIP | Yes | No | No | 2551THR | 2251TB |
| 2251EIS[19] | CLIP | No | Yes | No | ||
| 2251B | No | No | No | 1251B 2251 |
2351B-IV | |
| 2251TB | Yes | No | No | 2251T | 2351TB-IV | |
| 2251BR | No | No | Yes | DH200PL (with DNR) DH200RPL (with DNR) |
2351BR-IV |
Multi-criteria detectors
| Model | Protocol | Ionization sensor? | Photoelectric sensor? | Heat sensor? | Infrared sensor? | CO sensor? | Replaced | Replaced by |
| 2251TM | CLIP | No | Yes | Yes | No | No | 3251 | 2251TMB |
| 2251TMB | No | Yes | Yes | No | No | 1251B 2251TM |
2351TIR-IV | |
| 2251-COPTIR | No | Yes | Yes | Yes | Yes | 1251B | FC351 | |
| 3251[20] | CLIP | Yes | Yes | Yes | No | No | 2251TM |
| Model | Protocol | Type | Replaced | Replaced by |
| 5251P[21] | CLIP | Fixed temperature | 5551B | 5251B |
| 5251RP | CLIP | Rate-of-rise | 5551R | 5251RB |
| 5251B | Fixed temperature | 5251P | 5351B-IV | |
| 5251RB | Rate-of-rise | 5251RP | 5351RB-IV | |
| 5251H | High temperature | None | 5351H-IV |
Laser smoke detectors
| 7251[22] | Spot | 1251B LZR-1 |
7351 | |
| 7251DH | Duct | None | DNRHS |
Beam detectors
| Model | Integral sensitivity test? | Replaced | Replaced by |
| BEAM200[23] | No | ||
| BEAM200S | Yes |
Innovair duct detectors
| Model | Relay? | Replaced | Replaced by |
| DH200P[24] | No | DH500 | DH200PL |
| DH200RP | Yes | DH500ACDC | DH200RPL |
| DH200PL[25] | No | DH200P | DNR + 2251BR |
| DH200RPL | Yes | DH200RP | DNR + 2251BR |
Bases
| Model | Auxiliary function | Replaced | Replaced by |
| B210LP[26] | None | ||
| B224RB | Relay | ||
| B224BI | Isolator | ||
| B200S | Intelligent horn | None | |
| B200SR | Horn | B501BH B501BHT B501BH-2 B501BHT-2 |
| B200S-LF | Intelligent low frequency sounder | None | |
| B200SR-LF | Low frequency sounder | None |
Faraday rebranded 200 series products as part of the 8400 series, 9100 series, and 9200 series until 2004.[27][28][29]
Fire-Lite Alarms
350 series
Fire-Lite Alarms started rebranding the original 200 series in 2001 as the 350 series, replacing the 300 series.[30] The 350 series supported extended addressing for the MS-9600, but it did not support LiteSpeed.
| Fire-Lite model | System Sensor model | Replaced | Replaced by |
| SD350[31] | 2251 | SD300 | SD355 |
| SD350A | SD300A | SD355A | |
| SD350T | 2251T | SD300T | SD355T |
| SD350TA | SD300TA | SD355TA | |
| CP350[32] | 1251 | CP300 | CP355 |
| CP350A | CP300A | CP355A | |
| H350[33] | 5251P | None | H355 |
| H350R | 5251RP | None | H355R |
| D350P[34] | DH200P | None | D350PL |
| D350RP | DH200RP | None | D350RPL |
| D350PL[35] | DH200PL | D350P | D355PL |
| D350RPL | DH200RPL | D350RP | D355PL |
355 series
The 355 series replaced the 350 series in 2006.[36] The 355 series supported LiteSpeed, which was introduced in 2007 on the MS-9600LS.
| SD355[37] | 2251B | CP355 HFS-P SD350 |
SD365-IV |
| SD355A | SD350A | SD365A-IV | |
| SD355T | 2251TB | HFS-PT SD350T |
SD365T-IV |
| SD355TA | SD350TA | SD365TA-IV | |
| SD355R[38] | 2251BR | HFS-DPR | SD365R-IV |
| CP355[39] | 1251B | CP350 | 8100 + MMF-301 AD355 SD355 |
| CP355A | CP350A | ||
| H355[40] | 5251B | H350 HFS-T |
H365-IV |
| H355A | None | H365A-IV | |
| H355R | 5251RB | H350R | H365R-IV |
| H355RA | None | H365RA-IV | |
| H355HT | 5251H | None | H365HT-IV |
| H355HTA | None | H365HTA-IV | |
| AD355[41] | 2251TMB | CP355 | AD365-IV |
| AD355A | None | AD365A-IV | |
| BEAM355[42] | BEAM200 | None | |
| BEAM355S | BEAM200S | None | |
| D355PL[43] | DNR + 2251BR | D350PL D350RPL HFS-D |
D365PL |
FCI CLIP detectors
| Gamewell-FCI model | System Sensor model | Replaced | Replaced by |
| ASD-IL[44] | 1251 | ASD-I | ASD-IL2 |
| ASD-PL | 2251 | ASD-P | ASD-PL2 |
| ATD-L | 5251P | ATD | ATD-L2 |
| ATD-RL | 5251RP | ATD-R | ATD-RL2 |
| MCS-ACCLIMATE | 2251TM | None | MCS-ACCLIMATE2 |
| ASD-IL2[45] | 1251B | ASD-IL | ASD-IL2F |
| ASD-PL2[46] | 2251B | ASD-PL | ASD-PL2F |
| ASD-PTL2 | 2251TB | ASD-PTL2F | |
| ATD-L2[47] | 5251B | ATD-L | ATD-L2F |
| ATD-RL2 | 5251RB | ATD-RL | ATD-RL2F |
| ATD-HL2 | 5251H | None | ATD-HL2F |
| MCS-ACCLIMATE2[48] | 2251TMB | MCS-ACCLIMATE | MCS-ACCLIMATE2F |
| ADP[49] | DH200PL | ADPF | |
| ADP-R | DH200RPL | ADPRF |
SmartScan series
| SS-P[50] | 2251B | ASD-PL2F | |
| SS-M | 2251TB | ASD-PTL2F | |
| SS-APT[51] | 2251TMB | MCS-ACCLIMATE2F | |
| SS-I[52] | 1251B | ASD-IL2F | |
| SS-T[53] | 5251B | ATD-L2F | |
| SS-TR | 5251RB | ATD-RL2F | |
| SS-TH | 5251H | ATD-HL2F | |
| SS-L[54] | 7251 | ASD-LS | |
| SS-PD[55] | DH200PL | ||
| SS-PDR | DH200RPL | ||
| BD-SS[56] | BEAM200 | ABD-2F | |
| BDT-SS | BEAM200S | ABD-RT2F |
Velociti series
| ADPF[57] | DH200PL | ADP | DNR + ASD-PL2FR |
| ADPRF | DH200RPL | ADP-R | DNR + ASD-PL2FR + AOM-2RF |
| ASD-IL2F[58] | 1251B | ASD-IL2 SS-I |
AAD-8100 ASD-PL2F ASD-LS MCS-4-WARN MCS-ACCLIMATE2F |
| ASD-LS[59] | 7251 | ASD-IL2F SS-L |
ASD-LS3 |
| ASD-PL2F[60] | 2251B | ASD-IL2F ASD-PL2 HFS-P SS-P |
ASD-PL3-IV |
| ASD-PTL2F | 2251TB | ASD-PTL2 HFS-PT SS-M |
ASD-PTL3-IV |
| ASD-PL2FR[61] | 2251BR | ADPF (with DNR) ADPRF (with DNR + AOM-2RF) HFS-D (with DNR) HFS-DPR |
ASD-PL3R-IV |
| ATD-L2F[62] | 5251B | ATD-L2 HFS-T SS-T |
ATD-L3-IV |
| ATD-RL2F | 5251RB | ATD-RL2 SS-TR |
ATD-L3R-IV |
| ATD-HL2F | 5251H | ATD-HL2 SS-TH |
ATD-L3H-IV |
| ABD-2F[63] | BEAM200 | BD-SS | |
| ABD-RT2F | BEAM200S | BDT-SS | |
| MCS-ACCLIMATE2F[64] | 2251TMB | ASD-IL2F MCS-ACCLIMATE2 SS-APT |
MCS-PTIR-IV |
| MCS-4-WARN[65] | 2251-COPTIR | ASD-IL2F | MCS-COF3 |
Farenhyt series
Silent Knight introduced the Intelligent Device Protocol for Farenhyt systems in March 2006.[66]
| Honeywell model | System Sensor model | Replaced | Replaced by |
| IDP-ION[67] | 1251B | None | 8100 + IDP-MINIMON IDP-ACCLIMATE IDP-FIRE-CO IDP-PHOTO |
| IDP-PHOTO[68] | 2251B | HFS-P IDP-ION |
IDP-PHOTO-IV |
| IDP-PHOTO-T | 2251TB | HFS-PT | IDP-PHOTO-T-IV |
| IDP-PHOTOR | 2251BR | IDP-PDUCT (with DNR) IDP-PDUCT-R (with DNR + IDP-RELAY) HFS-D (with DNR) HFS-DPR |
IDP-PHOTO-R-IV |
| IDP-ACCLIMATE | 2251TMB | IDP-ION | IDP-PTIR-IV |
| IDP-BEAM | BEAM200 | None | |
| IDP-BEAM-T | BEAM200S | None | |
| IDP-HEAT | 5251B | HFS-T | IDP-HEAT-IV |
| IDP-HEAT-HT | 5251H | None | IDP-HEAT-HT-IV |
| IDP-HEAT-ROR | 5251RB | None | IDP-HEAT-ROR-IV |
| IDP-PDUCT[69] | DH200PL | None | DNR + IDP-PHOTOR |
| IDP-PDUCT-R | DH200RPL | None | DNR + IDP-PHOTOR + IDP-RELAY |
HFS series
Honeywell sold the 2251BR detector in DNR housing as the HFS-D, for use with the HFS series panels. The 2251BR was also sold on its own as the HFS-DPR.
XLS series
| TC806B1001[70] | 2251 | TC806B1076 | |
| TC806B1076[71] | 2251B | TC806B1001 TC807B1059 |
TC806B3010-IV |
| TC806B1084 | 2251TB | TC806B3104-IV | |
| TC806DNR | 2251BR | TC806DNR3000-IV | |
| TC807B1000[72] | 1251 | TC807B1059 | |
| TC807B1059 | 1251B | TC807B1000 | TC808B1076 TC840C1000 TC840M1021 TC846F1002 |
| TC808B1002 | |||
| TC808B1041 | 5251B | TC808B3011-IV | |
| TC808B1041CDN | 5251BA | TC808B3011CDN-IV | |
| TC808B1058 | 5251RB | TC808B3012-IV | |
| TC808B1058CDN | 5251RBA | TC808B3012CDN-IV | |
| TC808B1066 | 5251H | ||
| TC808B1066CDN | 5251HA | ||
| TC840C1000 | 2251-COPTIR | TC807B1059 | TC840C3206-IV |
| TC840M1021 | 2251TMB | TC807B1059 | TC840M3021-IV |
| TC846A1005 | |||
| TC846A1013 |
Johnson Controls
300 series
| Johnson Controls model | System Sensor model | Replaced | Replaced by |
| 1351J[73] | 1251 | 1951J | |
| 1351JA | 1951JA | ||
| 2351J | 2251 | 2951J | |
| 2351JA | 2951JA | ||
| 2351TJ | 2251T | 2951TJ | |
| 2351TJA | 2951TJA | ||
| 5351J | 5251P | 5951J | |
| 5351JA | 5951JA | ||
| 5351RJ | 5251RP | 5951RJ | |
| 5351RJA | 5951RJA | ||
| 7351J | 7251 | 1951J | J7351 |
| 7351JA | |||
| DH300PL | DH200PL | DNR + 2951JR | |
| DH300PLA | DNR + 2951JRA | ||
| DH300RPL | DH200RPL | ||
| DH300RPLA |
900 series
| 1951J | 1251B | 1351J | 2951J 2951TMJ 2951J-COPTIR 7351J 8251FJ |
| 1951JA | 1351JA | ||
| 2951J | 2251B | 1951J 2351J |
J2351-IV |
| 2951JA | 2351JA | ||
| 2951JR | 2251BR | DH300PL (with DNR) DH300RPL (with DNR) |
J2351R-IV |
| 2951JRA | DH300PLA (with DNR) DH300RPLA (with DNR) |
| 2951TJ | 2251TB | 2351TJ | J2351T-IV |
| 2951TJA | 2351TJA | ||
| 2951TMJ | 2251TMB | 1951J | |
| 2951TMJA | |||
| 2951J-COPTIR | 2251-COPTIR | 1951J | |
| 2951J-COPTIRA | |||
| 5951J | 5251B | 5351J | J5351-IV |
| 5951JA | 5351JA | ||
| 5951RJ | 5251RB | 5351RJ | J5351R-IV |
| 5951RJA | 5351RJA | ||
| 5951HJ | 5251H | None | J5351H-IV |
| 5951HJA | None |
700 series
The original Notifier rebrands of the 200 series were given the -751 suffix, and they did only supported CLIP. FlashScan detectors were introduced in 2000 together with the AFC-600 and could be identified with a "F" prefix.[74]
| Notifier model | System Sensor model | FlashScan capable? | Replaced | Replaced by |
| CPX-751[75] | 1251 | No | CPX-551 | FSI-751 |
| SDX-751 | 2251 | No | SDX-551 | FSP-751 |
| IPX-751[76] | 3251 | No | FAPT-751 | |
| LPX-751 | LZR-1 | No | None | FSL-751 |
| LPX-751L | 7251 | No | None | FSL-751 |
| FSI-751[77] | 1251 | Yes | CPX-751 | FSI-851 |
| FSP-751 | 2251 | Yes | SDX-751 | FSP-851 |
| FSP-751T | 2251T | Yes | SDX-551TH | FSP-851T |
| FAPT-751[78] | 2251TM | Yes | IPX-751 | FAPT-851 |
| FST-751[79] | 5251P | Yes | FDX-551 | FST-851 |
| FST-751R | 5251RP | Yes | FDX-551R | FST-851R |
| FSL-751 | 7251 | Yes | FSI-851 LPX-751 LPX-751L |
FSV-951R-IV |
| FSD-751P[80] | DH200P | Yes | FSD-751PL | |
| FSD-751RP | DH200RP | Yes | FSD-751RPL | |
| FSD-751PL[81] | DH200PL | Yes | FSD-751P | DNR + FSP-851R |
| FSD-751RPL | DH200RPL | Yes | FSD-751RP | DNR + FSP-851R + FRM-1 |
800 series
The 800 series detectors supported both CLIP and FlashScan. These were released in 2003.[82]
| Notifier model | System Sensor model | Replaced | Replaced by |
| FAPT-851 | 2251TMB | FAPT-751 FSI-851 |
FPTI-951-IV |
| FSI-851 | 1251B | FSI-751 | FAPT-851 FSA-8000 FSC-851 FSL-751 FSP-851 |
| FSP-851 | 2251B | FSI-851 FSP-751 |
FSP-951-IV |
| FSP-851T | 2251TB | FSP-751T | FSP-951T-IV |
| FSP-851R[83] | 2251BR | FSD-751PL (with DNR) FSD-751RPL (with DNR) |
FSP-951R-IV |
| FST-851 | 5251B | FST-751 | FSP-951-IV |
| FST-851R[84] | 5251RB | FST-751R | FSP-951R-IV |
| FST-851H | 5251H | None | FSP-951H-IV |
| FSC-851[85] | 2251-COPTIR | FSI-851 | FCO-951-IV |
FireWarden detectors
Notifier produced a separate series of detectors for use with FireWarden panels.
| ND-100R[86] | DH200RPL | DNR + NP-100R | |
| NH-100[87] | 5251B | HFS-T | |
| NH-100A | |||
| NH-100R | 5251RB | ||
| NH-100RA | |||
| NI-100[88] | 1251B | NP-100 | |
| NI-100A | |||
| NP-100[89] | 2251B | HFS-P NI-100 |
| NP-100A | |||
| NP-100T | 2251TB | HFS-PT | |
| NP-100TA | |||
| NP-100R[90] | 2251BR | HFS-D (with DNR) HFS-DPR ND-100R (with DNR) |
Silent Knight started rebranding 200 series devices in 2009.[91]
| Silent Knight model | System Sensor model | Replaced | Replaced by |
| SK-PHOTO | 2251B | HFS-P SK-ION |
SK-PHOTO-W |
| SK-PHOTO-T | 2251TB | HFS-PT | SK-PHOTO-T-W |
| SK-PHOTOR[92] | 2251BR | HFS-DPR | SK-PHOTO-R-W |
| SK-ION | 1251B | None | 8100 + SK-MINIMON SK-ACCLIMATE SK-FIRE-CO SK-PHOTO |
| SK-HEAT | 5251B | HFS-T | SK-HEAT-W |
| SK-HEAT-HT | 5251H | None | SK-HEAT-HT-W |
| SK-HEAT-ROR | 5251RB | None | SK-HEAT-ROR-W |
| SK-ACCLIMATE | 2251TMB | SK-ION | SK-PTIR-W |
| SK-DUCT | DNR + 2251BR | HFS-D | SK-DUCT-W |
| SK-BEAM | BEAM200 | None | |
| SK-BEAM-T | BEAM200S | None |
- ↑ https://nfpa.access.preservica.com/uncategorized/IO_e739b0ac-5683-41d8-8725-3d1426de8e70/
- ↑ https://nfpa.access.preservica.com/uncategorized/IO_07a0ad96-a2e8-4dfb-9596-317511ba151b/
- ↑ "sitemap page" System Sensor. Archive 2000-07-07 vs. 2000-10-17
- ↑ https://web.archive.org/web/20001209133400/http://www.systemsensor.com/Intelligent/acclimat.htm
- ↑ https://web.archive.org/web/20040306064955/http://systemsensor.com:80/html/id.html?search=Intelligent%20Smoke%20Detector
- ↑ "Pinnacle - Ultra High Sensitivity Laser Smoke Detector" (A05-0347-000). System Sensor (2002).
- ↑ "Intelligent Detection" System Sensor. Archive 2003-06-22 vs. 2003-10-19
- ↑ "Intelligent Detection" System Sensor. Archive 2003-12-24 vs. 2004-04-05
- ↑ https://web.archive.org/web/20080110051642/http://www.systemsensor.com/html/id.html?search=Intelligent%20Smoke%20Detector
- ↑ https://web.archive.org/web/20110110232350/http://www.systemsensor.com/html/id.html?search=Intelligent%20Smoke%20Detector
- ↑ "Intelligent Detection" System Sensor. Archive 2007-11-10 vs. 2008-01-10
- ↑ https://web.archive.org/web/20090729061302/http://www.systemsensor.com:80/html/id.html?search=base
- ↑ "B200S Intelligent Sounder Base" (A05-0455-000). System Sensor (April 2009).
- ↑ "Intelligent Detection" System Sensor. Archive 2009-07-29 vs. 2010-08-23
- ↑ "Documentation" Silent Knight. Archive 2015-01-12 vs. 2015-02-06
- ↑ "Ionization Smoke Detector: Remove, Recycle, Replace." (SPFL78501). System Sensor (2015).
- ↑ https://web.archive.org/web/20000620173647/http://www.systemsensor.com/Intelligent/plug.htm
- ↑ https://web.archive.org/web/20031224232554/http://www.systemsensor.com/html/id.html?search=Intelligent%20Smoke%20Detector
- ↑ https://web.archive.org/web/20000821185848/http://www.systemsensor.com/Intelligent/intrinsi.htm
- ↑ https://web.archive.org/web/20000821185948/http://www.systemsensor.com/Intelligent/multi.htm#
- ↑ https://web.archive.org/web/20000821190341/http://www.systemsensor.com/Intelligent/thermal.htm
- ↑ "Pinnacle Low-Profile Plug-in Intelligent Laser Smoke Detector" (A05-0314-001). System Sensor (October 2001).
- ↑ "Model BEAM200(S) Single-ended Reflected Type Beam Smoke Detector" (A05-0364-000). System Sensor (January 2004).
- ↑ "Innovair™ 200 Series Intelligent Duct Smoke Detectors" (A05-0280-001). System Sensor (January 2000).
- ↑ "Innovair Intelligent Low-Flow Duct Smoke Detectors" (A05-0353-000). System Sensor (July 2003).
- ↑ https://web.archive.org/web/20001020100231/http://systemsensor.com/Intelligent/bases.htm
- ↑ https://tecumsehtech.com/Detectors-and-Modules
- ↑ https://web.archive.org/web/20040219083128/http://www.faradayllc.com/products_addressable.html
- ↑ https://web.archive.org/web/20040401233430/http://faradayfirealarms.com/products_initiating.html
- ↑ "Addressable Devices" Fire-Lite Alarms. Archive 2001-03-08 vs. 2001-04-29
- ↑ "SD350(A)/SD350T(A) Addressable Photoelectric Detectors" (DF-52149). Fire-Lite Alarms (May 3, 2001).
- ↑ "CP350 Intelligent Addressable Ionization Detector" (DF-52158). Fire-Lite Alarms (May 3, 2001).
- ↑ "H350/H350R Intelligent Addressable Thermal (Heat) Detectors for use with MS-9600" (DF-52167). Fire-Lite Alarms (June 25, 2001).
- ↑ "D350P/D350RP Intelligent Addressable Photoelectronic Duct Smoke Detector" (DF-52176). Fire-Lite Alarms (May 2, 2001).
- ↑ "D350PL(A) and D350RPL(A) Intelligent Low-Flow Photoelectric Duct Smoke Detectors" (DF-52398). Fire-Lite Alarms (January 11, 2005).
- ↑ "FireLite Systems - Products" Fire-Lite Alarms. Archive 2006-04-20 vs. 2006-09-04
- ↑ "SD355(A)/SD355T(A) Addressable Photoelectric Smoke Detectors" (DF-52384). Fire-Lite Alarms (July 14, 2004).
- ↑ "DNR-InnovairFlex Intelligent Non-Relay Photoelectric Duct Smoke Detector" (df-60430). Fire-Lite Alarms (July 13, 2011).
- ↑ "CP355(A) Intelligent Addressable Ionization Smoke Detectors" (DF-52383). Fire-Lite Alarms (July 14, 2004).
- ↑ "H355 (A) Series Intelligent Addressable Thermal (Heat) Detectors for MS-9600, MS-9200UD" (DF-52385). Fire-Lite Alarms (July 14, 2004).
- ↑ "AD355 (A) "Adapt" Multi-Sensor Low-Profile Intelligent Detectors" (DF-52386). Fire-Lite Alarms (July 14, 2004).
- ↑ "BEAM355 and BEAM355S Single-Ended, Reflected-Type Addressable Beam Smoke Detectors" (DF-52408). Fire-Lite Alarms (January 6, 2005).
- ↑ https://web.archive.org/web/20120109170353/http://firelite.com/products/innovair.htm
- ↑ "Analog Addressable Sensors" (9020-0471). Fire Control Instruments (2000).
- ↑ "ASD-IL2" (9020-0558). Fire Control Instruments (2003).
- ↑ "ASD-PL2" (9020-0559). Fire Control Instruments (2003).
- ↑ "ATD-L2" (9020-0560). Fire Control Instruments (2003).
- ↑ "MCS-ACCLIMATE2" (9020-0561). Fire Control Instruments (2003).
- ↑ "ADP Series" (9020-0567). Fire Control Instruments (2003).
- ↑ "SS-P and SS-M Intelligent Addressable Plug-In Photoelectric Smoke Detectors with SmartScan®" (CS-2458). Gamewell (May 13, 2005).
- ↑ "SS-APT Acclimate™ Multi-Sensor Smoke Detector Low-Profile, Intelligent, Addressable" (CS-2462). Gamewell (October 21, 2004).
- ↑ "SS-I Intelligent Addressable Plug-In Ionization Smoke Detector" (CS-2459). Gamewell (October 21, 2004).
- ↑ "SS-T Series Intelligent Addressable Plug-In Thermal (Heat) Detectors" (CS-2460). Gamewell (October 21, 2004).
- ↑ "SS-L Laser Smoke Detector" (CS-2461). Gamewell (October 21, 2004).
- ↑ "SS-PD and SS-PDR Intelligent Low-Flow Photoelectric Duct Smoke Detectors" (CS-2463). Gamewell (October 21, 2004).
- ↑ "BD-SS and BDT-SS Single-Ended, Reflected-Type, Addressable Beam Smoke Detector with SmartScanTM" (CS-2516). Gamewell (April 14, 2005).
- ↑ "ADPF and ADPRF" (9020-0622). Fire Control Instruments (2005).
- ↑ "ASD-IL2F" (9020-0619). Fire Control Instruments (2005).
- ↑ "ASD-LS" (9020-0525). Fire Control Instruments (2002).
- ↑ "ASD-PL2F and ASD-PTL2F" (9020-0617). Fire Control Instruments (2005).
- ↑ "Velociti® Series ASD-PL2F, ASD-PTL2F and ASD-PL2FR" (9020-0617). Gamewell-FCI (2010).
- ↑ "ATD-L2F, ATD-RL2F, and ATD-HL2F" (9020-0620). Fire Control Instruments (2005).
- ↑ "Velociti® Series ABD-2F and ABD-RT2F" (9020-0623). Gamewell-FCI (2008).
- ↑ "MCS-ACCLIMATE2F" (9020-0618). Fire Control Instruments (2005).
- ↑ "Velociti® Series MCS-4-Warn" (9021-60672). Honeywell Gamewell FCI (November 2017).
- ↑ https://web.archive.org/web/20070520191545/http://www.farenhyt.com/htmfiles/pressrelease.htm#March2006
- ↑ "Addressable Devices with Intelligent Device Protocol (IDP)" (350361). Silent Knight (2015).
- ↑ "Supplement to Farenhyt Manuals" (LS10213-152FH-E:J). Honeywell (February 17, 2022).
- ↑ "IDP-Pduct/IDP-Pduct-R" (350284). Silent Knight (2008).
- ↑ https://i.ebayimg.com/images/g/dK8AAOSwZrJgLVRo/s-l1600.jpg
- ↑ "Detector/Base Compatibility Chart". System Sensor (October 30, 2014).
- ↑ https://i.ebayimg.com/images/g/UNYAAOSwGo1j39Dv/s-l1600.jpg
- ↑ "Johnson Controls IFC/NOTIFIER Compatibility Document" (LS10200-000NF-E:B). Notifier (January 11, 2022).
- ↑ "CSFM Listing Sheets" Notifier Fire Systems. Archive 2000-06-15 vs. 2000-08-21
- ↑ "CPX-751 and SDX-751 Low-Profile Intelligent Plug-in Smoke Detectors" (DN-7086). Notifier (December 16, 2005).
- ↑ https://web.archive.org/web/20000523135951/http://www.notifier.com/advanced_detection.htm
- ↑ "FSI-751 and FSP-751/751T Low-Profile Intelligent Plug-in Smoke Detectors with FlashScan®" (DN-6714). Notifier (November 13, 2002).
- ↑ "FAPT-751 Acclimate Plus™ Multi-Sensor Low-Profile Intelligent Detector" (DN-6833). Notifier (April 1, 2003).
- ↑ "FST-751 Series Intelligent Thermal (Heat) Detectors with FlashScan®" (DN-6716). Notifier (October 9, 2001).
- ↑ "FSD-751P and FSD-751RP Intelligent Photoelectric Duct Smoke Detectors with FlashScan®" (DN-6821). Notifier (June 5, 2001).
- ↑ "FSD-751PL and FSD-751RPL Intelligent Low-Flow Photoelectric Duct Smoke Detectors with Flashscan®" (DN-6955). Notifier (May 24, 2004).
- ↑ "Data Sheets" Notifier. Archive 2003-02-25 vs. 2003-04-19
- ↑ "FSP-851, FSP-851T, & FSP-851R Intelligent Plug-In Photoelectric" (dn-6935). Notifier (March 12, 2010).
- ↑ "FST-851 Series Intelligent Thermal (Heat) Detectors with FlashScan®" (DN-6936). Notifier (April 1, 2003).
- ↑ "FSC-851(A) IntelliQuad™ Advanced Multi-Criteria Detector with four unique sensing elements" (DN-60412:B). Notifier (August 25, 2010).
- ↑ "ND-100R Low-Flow Photoelectric Duct Smoke Detector with Relay for FireWarden-100" (DN-7006). Notifier (October 20, 204).
- ↑ "NH-100 Series Intelligent Addressable Thermal (Heat) Detectors for FireWarden-100" (DN-6997). Notifier (October 20, 2004).
- ↑ "NI-100(A) Intelligent Addressable Ionization Detectors" (DN-6996). Notifier (September 8, 2004).
- ↑ "NP-100(A) and NP-100T(A) Addressable Photoelectric Detectors" (DN-6995). Notifier (October 20, 2004).
- ↑ "NP-100(A), NP-100T(A), NP-100R(A) Addressable Photoelectric Detectors for the FireWarden Series" (dn-6995). Notifier (March 12, 2010).
- ↑ "Product Guide" Silent Knight. Archive 2009-02-19 vs. 2010-06-01
- ↑ "SK-PHOTO, SK-PHOTO-T, and SK-PHOTOR Intelligent Photoelectric Smoke Detectors" (350118). Honeywell Silent Knight (November 2017).