Heat detector
A heat detector is a device that detects heat. Heat detectors are often used as initiating devices on fire alarm systems.
Operation
Conventional Heat Detectors are often a mixture of fixed temperature and rate-of-rise. Fixed detectors work like pull stations. When they reach a certain temperature, a link in the device melts away, and a spring causes the short. Many fixed heat detectors cannot be re-used, and must be replaced if tripped. Some newer detectors use a thermistor which when cooled, allows the device to be reset.
Rate of Rise, however, will use power of the IDC to activate. When the temperature increases at a specific rate, the device will go into an active state. These can be reset and reused when they cool down.
Most common, modern conventional heat detectors are a combination of both fixed and rate of rise. If the rate of rise portion activates, it can be re-used. However, if the fixed portion activates, the device will need to be replaced.
Heat detectors in the intelligent sense are really just heat sensors. Upon a certain temperature, or rate of rise in temperature, the detector will let the panel know that things are getting warm, and the panel will activate.
Though this isn't what we are seeing in the industry yet, it is not far fetched that a heat detector might be able to be used in any application, and a setting be made in the panel for the temperature it activates, rather than the detector.
Coverage types
Spot-type detectors
Linear detectors
Sensing technologies
Fusible element detectors
Rate-of-rise diaphragms
Rate-compensation detectors
Thermistors
Open area protection
NFPA 72 includes requirements for heat detector placement when heat detectors are used to provide open area protection.[1]: 17.6.3
NFPA codes require heat detection in a few situations. Note sprinklers may be used in place of heat detectors, even if they are not supervised, and heat detection required by NFPA 101 and NFPA 5000 may also be substituted by a water mist system.[2]: 13.3.1.6 [3]: 9.7.1.4, 9.8.2.3 [4]: 55.3.1.4, 55.5.2.3
- Pull stations may be omitted from educational occupancies under certain conditions, including the presence of heat detection or approved alternatives in all assembly areas and shops/laboratories.[2]: 13.7.2.3.2.3.1, 13.7.2.4.2.3.1 [3]: 14.3.4.2.3.1, 15.3.4.2.3.1 [4]: 17.3.4.2.3.1
- Existing apartment buildings utilizing "Option 2" must provide open area heat detection inside living areas.[2]: 13.7.2.18.4.2(2) [3]: 31.3.4.4.2(2)
- Sprinklers may be omitted from attics of new residential board and care occupancies with 16 or fewer residents and all existing residential board and care occupancies if heat detection is provided.[2]: 13.3.2.19.2.7.2(1), 13.3.2.20.1.4.2(1), 13.3.2.20.4.2(1) [3]: 32.2.3.5.7.2(1), 33.2.3.5.7.2(1), 33.3.3.5.4.2(1) [4]: 26.2.3.4.5, 26.2.3.4.6, 26.2.3.5.6.2(1)
The I-Codes also require open area heat detection in a few situations.
- Group R-4 Condition 2 occupancies may omit sprinklers from attics if heat detection is provided.[5]: 903.3.1.2.3 [6]: 903.3.1.2.3
- Pull stations may be omitted from educational occupancies under certain conditions, including the presence of heat detection or approved alternatives in all assembly areas and shops/laboratories.[5]: 907.2.3 [6]: 907.2.3
- Heat detection must be provided in all areas that would otherwise require smoke detection but are unsuitable for smoke detectors. Note that for this specific requirement, sprinklers may be used as an alternative unless the detection system is required for a delayed/controlled egress lock or elevator recall.[5]: 907.4.3 [6]: 907.4.3
- A sprinkler system, smoke detection system, or heat detection system must be provided in any building with delayed egress locks.[5]: 1010.2.12 [6]: 1010.2.12
Other detector locations
Elevators
Heat detectors are often installed in elevator shafts and machine rooms for power shutdown before an adjacent sprinkler activates, if such sprinkler operation would be dangerous with a running elevator. Additionally, heat detectors are often used in place of smoke detectors for elevator recall when conditions are not suitable for smoke detectors.
Fire alarm system protection
NFPA 72 and the I-Codes require a smoke detector to be installed above every FACP, power supply, and communicator located in an area not continuously occupied, but if ambient conditions are not suitable for a smoke detector, a heat detector is permitted to be used instead.[1]: 10.4.5 [5]: 907.4.1 [6]: 907.4.1
- ↑ 1.0 1.1 National Fire Alarm and Signaling Code® (NFPA 72, 2025)
- ↑ 2.0 2.1 2.2 2.3 Fire Code (NFPA 1, 2024)
- ↑ 3.0 3.1 3.2 3.3 Life Safety Code (NFPA 101, 2024)
- ↑ 4.0 4.1 4.2 Building Construction and Safety Code (NFPA 5000, 2024)
- ↑ 5.0 5.1 5.2 5.3 5.4 International Building Code (2024)
- ↑ 6.0 6.1 6.2 6.3 6.4 International Fire Code (2024)