System Sensor i3 series
8.5-35 VDC
2001
System Sensor 100 series |
"title": "i<sup>3</sup> series",
"System Sensor i3.webp"
The System Sensor i3 series is a series of conventional detectors.
The i3 series was introduced in 2001 as a replacement for the standard 100 series Direct-Wire smoke detectors.[1] The original series consisted of the 2W-B, 2WT-B, 4W-B, and 4WT-B detectors, as well as the 2W-MOD interface required for 2-wire detectors on existing panels; the 2W-MOD had a similar design to the 500 series modules. The Fire-Lite MS-2 and MS-4 were also introduced at this time with integrated i3 protocol support, removing the need for the 2W-MOD on these panels.[2]
In 2002, System Sensor introduced sounder and relay models to replace the specialty 100 series Direct-Wire detectors. The 2W-MOD was not compatible with the 2WTA-B and 2WTR-B, so the 2W-MOD2 was released as a replacement.[3]
Around 2014, the MOD2W was introduced as a successor to the 2W-MOD2 with a similar design to the i4 modules.[4]
In December 2020, the i3 detectors were updated to comply with the 7th edition of UL 268.[citation needed]
Operation
The detector is microprocessor based. The i3 protocol supported by a select amount of Honeywell panels allows for usage of the MAINTENANCE light to indicate certain faults with the detector on a normal conventional zone. Faults that fall under maintenance include operating out of it's temperature range (Overheat at 135F, freezing at 41F), and the detector falling out of sensitivity which indicates the requirement for cleaning.
On two-wire i3s, the detector is put in alarm by reversing the poles. This means you will need a panel that supports this. An i3 loop test/maintenance module can be used otherwise. DO NOT power it with batteries. This will result in frying the detector.
This table lists the operation modes of the i3.
| Mode | Green LED | Red LED |
| Detector Power-Up | Blink 10 Seconds | Blink 10 Seconds |
| Normal Operation | Blink 5 Seconds | |
| Alarm | Solid | |
| Freeze Trouble | Blink 10 Seconds | |
| Out of Sensitivity | Blink 5 Seconds |
| Model | Wiring | Type | Relay? | Horn? | Replaced |
| 2W-B | 2-wire | Photoelectric | No | No | 1400 2100S 2400 |
| 2WT-B | 2-wire | Photoelectric with thermal | No | No | 2100TS 2112/24TSRB (with 2W-MOD) 2400TH 2451TH |
| 2WTA-B | 2-wire | Photoelectric with thermal | No | Yes | 2100AT |
| 2WTR-B | 2-wire | Photoelectric with thermal | Yes | No | 2100TR |
| 4W-B | 4-wire | Photoelectric | No | No | 1412B 1424 2112/24S |
| 4WT-B | 4-wire | Photoelectric with thermal | No | No | 2112/24TS 2451TH |
| 4WTA-B | 4-wire | Photoelectric with thermal | No | Yes | 2112/24AT |
| 4WTR-B | 4-wire | Photoelectric with thermal | Yes | No | 1412B 1424 2112/24R 2112/24TR 2412B 2412THB 2424 2424TH |
| 4WTAR-B | 4-wire | Photoelectric with thermal | Yes | Yes | 2112/24ATR |
| 4WITAR-B | 4-wire | Thermal with isolated local photoelectric alarm | Yes | Yes | 2112/24AITR |
Accessories
2-wire interface modules
The 2-wire interface modules (2W-MOD, 2W-MOD2, and MOD2W) act as sub controllers for i3 detectors.[5] They can be used for panels that don't support i3s or two wire detectors. It supports the EZ WALK TEST feature of the i3 and has 4 indicator lights to annunciate normal activity, walk test indication, wiring faults, smoke sensitivity plus freeze faults, smoke and CO alarms. A trouble relay is provided for the maintenance faults as with a 24V resettable power input, and alarm. Class A is supported.
SENS-RDR
A sensitivity reader tool to measure sensitivity on the i3 detectors, plus the 2151 & 2151T 100 series detectors made after April 2006.[6] It is an infared optical interface that reads the sensitivity & status data automatically shot by the detector every ten seconds. Depending on circumstances the reader will display "GOOD", "SERVICE", and "REPLACE".
RRS-MOD
The RRS-MOD reversing relay/synchronization module helps enable the sounder equipped on select i3s as if they were a part of the actual alarm system. This is done by tying it to the NAC circuit.[7]
RT
Specialized removal tool for i3 detectors.
A77-AB2
"i3 Retrofit Adapter Ring" - This is essentially a lower profile mounting plate for the i3. usually used when retrofitting where a larger smoke detector once was.
Faraday briefly rebranded the standard i3 devices as part of the 8400 series until 2004.
DMP
DMP rebrands the i3 detectors as their own addressable models (2W‑BLX, 2WT‑BLX) for the 12V LX-BUS addressable protocol. Detector heads have a DMP sticker put on top of the normal System Sensor one noting no physical difference outside of that, but the detector bases include a DMP monitor module sandwiched in between the screw terminals. Of note is that techs frequently remove this monitor as to make the detector onto a conventional zone rather.
| Monaco model | System Sensor model | Replaced | Replaced by |
| 723-340-00[8] | 2W-B | Still in production | |
| 723-340-01 | 2WT-B | Still in production | |
| 723-508-00 | 4W-B | Still in production | |
| 723-508-01 | 4WT-B | Still in production |
Honeywell/Resideo
Honeywell/Resideo produces the 5193 series V-Plex Addressable smoke detectors which are basically addressable i3 detectors.[9] They are meant for the Honeywell Vista Series of addressable Burg/Fire panels. These detectors lack dials to set address and are programmed through the panel.
- ↑ "News page" System Sensor. Archive 2001-08-10 vs. 2001-10-14
- ↑ "Control Panels Page 1" Fire-Lite Alarms. Archive 2001-08-15 vs. 2001-12-13
- ↑ "i3 Series Photoelectric Smoke Detector" (I56-2170-010). System Sensor (February 20, 2017).
- ↑ "i3 Series 2-Wire Loop Test/Maintenance Module" (MDDS29501). System Sensor (February 2014).
- ↑ https://prod-edam.honeywell.com/content/dam/honeywell-edam/hbt/en-us/documents/manuals-and-guides/installation-guides/moved-ss/MOD2W_Manual_I56-4001.pdf?download=false
- ↑ https://prod-edam.honeywell.com/content/dam/honeywell-edam/hbt/en-us/documents/manuals-and-guides/user-manuals/SENS-RDR_Manual_I56-1801.pdf
- ↑ https://prod-edam.honeywell.com/content/dam/honeywell-edam/hbt/en-us/documents/literature-and-specs/datasheets/RRS-MOD_DataSheet_A05-0350.pdf
- ↑ "Monaco Products Catalog". Monaco Enterprises (September 2024).
- ↑ https://buildings.honeywell.com/us/en/products/by-category/sensors/smoke-detectors/5193-series-v-plex-addressable-smoke-detector