System Sensor 500 series
System Sensor 200 series
"title": "500 series",
The System Sensor 500 series is a series of addressable detectors and modules.
The 500 series was introduced in 1987 together with the 400 series and Fire-Lite AM 2020 (more commonly known under the Notifier brand).
In 1992, System Sensor introduced the M500X isolator module.[1]
In 1999, the 1551B and 2551HR were designated exclusively for duct use, and the remaining detectors were discontinued and replaced with 200 series equivalents.[2][3] The address selection dials on the modules were also updated at this time to provide space for extended addressing, and the M500CH was replaced with separate M500R and M500S modules depending on whether supervision was required.
The 1551B/2551HR detectors and DH500 duct housings were discontinued around 2000 due to the release of the Innovair duct detectors.
In 2017, the module faceplates were updated to a bright white color, similar to the white L-Series devices. Replacement faceplates in both white and ivory were provided for retrofit applications.[4]
| Model | Listing | Replaced by |
| 1551B[5] | UL | 1251 |
| 1551AB | ULC |
| Model | Heat sensor? | Listing | Replaced by |
| 2551HR | No | UL | 2251 |
| 2551AHR | No | ULC | |
| 2551THR | Yes | UL | 2251T |
| 2551TAHR | Yes | ULC |
| Model | Type | Listing | Replaced by |
| 5551B | Fixed temperature | UL | 5251P |
| 5551AB | Fixed temperature | ULC | |
| 5551R | Rate-of-rise | UL | 5251RP |
| 5551RA | Rate-of-rise | ULC |
Detector bases
| Model | Flanges? | Auxiliary function | Listing | Replaced by |
| B501 | No | None | UL/ULC | B501-IV |
| B501B | Yes | None | UL/ULC | B210LP |
| B524RB | Yes | Relay | UL | B224RB |
| B524RBA | Yes | Relay | ULC | |
| B524BI | Yes | Isolator | UL | B224BI |
| B524BIA | Yes | Isolator | ULC | |
| B501BH | No | Sounder | UL | B200SR |
| B501BHA | No | Sounder | ULC | B200SR |
| B501BHT[6] | Temporal sounder | UL | B200SR | |
| B501BHTA | Temporal sounder | ULC | B200SR | |
| B501BH-2 | Sounder | UL | B200SR | |
| B501BH-2A | Sounder | ULC | B200SR | |
| B501BHT-2 | Temporal sounder | UL | B200SR | |
| B501BHT-2A | Temporal sounder | ULC | B200SR | |
| DH500 | N/A | Duct housing | UL | DH200P (with 1551B or 2551HR) |
| DH500A | N/A | Duct housing | ULC | |
| DH500ACDC | N/A | Duct housing with relay | UL | DH200RP (with 1551B or 2551HR) |
| DH500ACDCA | N/A | Duct housing with relay | ULC |
Modules
| Model | Size | Function | Listing | Replaced | Replaced by |
| M500MB | 4-inch | Monitor | UL | ||
| M500MAB | 4-inch | Monitor | ULC | ||
| M500M-4-20[7] | 4-inch | 4-20 mA analog input | UL | ||
| M500C[8] | 4-inch | Control | UL | M500CH | |
| M500CH | 4-inch | Control | UL | M500C | M500R M500S |
| M500CHA | 4-inch | Control | ULC | ||
| M500X | 4-inch | Isolator | UL/ULC | ||
| M501M | Small | Monitor | UL | ||
| M501MA | Small | Monitor | ULC | ||
| M502M[9] | 4-inch | Zone interface | UL | ||
| M502MA | 4-inch | Zone interface | ULC | ||
| M503ME | Small | Monitor | UL | ||
| M500R | 4-inch | Relay | UL | DH200RPL (with DNR + 2251BR) M500CH |
| M500S | 4-inch | Supervised control | UL | M500CH |
Faraday rebranded 500 series products as part of the 8400 series, 9100 series, and 9200 series until 2004.[10][11][12]
Fire-Lite Alarms
| Fire-Lite model | System Sensor model | Replaced | Replaced by |
| CP300[13] | 1551B | CPID[14] | CP350 |
| CP300A | 1551AB | None | CP350A |
| SD300[15] | 2551HR | SDID | SD350 |
| SD300A | 2551AHR | None | SD350A |
| SD300T | 2551THR | SDID-T | SD350T |
| SD300TA | 2551TAHR | None | SD350TA |
| C304[16] | M500CH | None | |
| C304A | M500CHA | None | |
| I300 | M500X | DCID DCID24 |
| I300A | M500X | None | |
| M300 | M500MB | IZ412 IZ424 RIZ-1 |
| M300A | M500MAB | None | |
| M301 | M501M | None | |
| M301A | M501MA | None | |
| M302 | M502M | IZ412 IZ424 |
| M302A | M502MA | None |
FCI CLIP devices
| Gamewell-FCI model | System Sensor model | Replaced | Replaced by |
| ASD-I[17] | 1551B | ASD-IL | |
| ASD-P[18] | 2551HR | ASD-PL | |
| ATD[19] | 5551B | ATD-L | |
| ATD-R | 5551R | ATD-RL | |
| AMM-2[20] | M501M | AMM-2F | |
| AMM-2I | M500DM | AMM-2IF | |
| AMM-4 | M500M | AMM-4F | |
| AMM-4S | M502M | AMM-4SF | |
| AOM-2R | M500R | AOM-2RF | |
| AOM-2S | M500S | AOM-2SF |
SmartScan series
| SCE-SS[21] | M500S | AOM-2SF | |
| RCE-SS | M500R | AOM-2RF | |
| PIDP-SS[22] | M500M | AMM-4F | |
| PID-SS | M501M | AMM-2F | |
| CZI-SS | M502M | AMM-4SF | |
| DPID-SS | M500DM | AMM-2IF | |
| SS-LI[23] | M500X | M500X |
Velociti series
| AMM-2F[24] | M501M | AMM-2 PID-SS |
| AMM-2IF[25] | M500DM | AMM-2I DPID-SS ZDM-D |
| AMM-4F[26] | M500M | AMM-4 PIDP-SS ZDM VZM |
| AMM-4SF[27] | M502M | AMM-4S CZI-SS ZDM ZDM-D VZM |
| AOM-2RF[28] | M500R | ADPRF (with DNR + ASD-PL2FR) AOM-2R RCE-SS SRB-6 TBZ |
| AOM-2SF[29] | M500S | AOM-2S SCE-SS BCM-6 |
| AOM-TELF[30] | M500FP | ||
| AOM-MUXF | M500DR | ||
| TC810S1000[31] |
Farenhyt series
| Honeywell model | System Sensor model | Replaced | Replaced by |
| IDP-MONITOR[32] | M500MB | SD500-AIM | Still in production |
| IDP-MINIMON | M501M | HFS-MM SD500-MIM |
| IDP-MONITOR-2 | M500DM | None | Still in production |
| IDP-RELAY | M500R | HFS-MR IDP-PDUCT-R (with DNR + IDP-PHOTOR) SD500-ARM SD505-DUCTR (with DNR + IDP-PHOTO-R-IV) |
| IDP-RELAYMON-2 | M500DMR | None | Still in production |
| IDP-CONTROL | M500S | SD500-ANM | Still in production |
| IDP-ZONE | M502M | SD500-SDM | Still in production |
| IDP-ISO | M500X | SD500-LIM | Still in production |
HFS series
Honeywell rebranded the M501M and M500R modules as part of the HFS series.
XLS series
| TC809A1059[33] | M500MB | Still in production | |
| TC809A1059CDN | M500MAB | Still in production | |
| TC809B1008 | M501M | Still in production | |
| TC809B1008CDN | M501MA | Still in production | |
| TC809D1004 | M500DM | Still in production | |
| TC809D1004CDN | M500DMA | Still in production | |
| TC810N1013 | M500S | Still in production | |
| TC810N1013CDN | M500SA | Still in production | |
| TC810S1000 | Still in production | ||
| TC810S1000CDN | Still in production | ||
| TC810T1000 | M500FP | Still in production | |
| TC810T1000CDN | M500FPA | Still in production | |
| TC810R1024 | M500R | Still in production | |
| TC810R1024CDN | M500RA | Still in production | |
| TC811A1006[34] | M500X | Still in production | |
| TC811A1014[35] | M500XA | Still in production | |
| TC822A1010 | M500DMR | Still in production | |
| TC822A1010CDN | Still in production | ||
| TC841A1000 | M502M | Still in production | |
| TC841A1000CDN | M502MA | Still in production |
Monaco Enterprises rebranded CLIP-only 500 series devices as "Type I" devices and devices capable of the advanced protocol (AP) as "Type II" devices. Monaco also rebranded the M500X as the 729-140-00, and this device was not labeled by either type because it does not directly interact with the SLC communications.[36]
Type I
| Monaco model | System Sensor model | Replaced | Replaced by |
| 729-127-00 | B501 | 729-215-00 | |
| 729-142-00 | M500MB | 729-217-00 | |
| 729-143-00 | M501M | 729-218-00 | |
| 729-144-00 | M502M | 729-219-00 | |
| 729-158-00 | M500S | 729-225-00 | |
| 729-159-00 | M500R | 729-221-00 | |
| 729-182-00 | M500DM | 729-220-00 |
Type II
| 729-217-00 | M500MB | 729-142-00 | Still in production |
| 729-218-00 | M501M | 729-143-00 | Still in production |
| 729-219-00 | M502M | 729-144-00 | Still in production |
| 729-220-00 | M500DM | 729-182-00 | Still in production |
| 729-221-00 | M500R | 729-159-00 | Still in production |
| 729-225-00 | M500S | 729-158-00 | Still in production |
| Notifier model | System Sensor model | Replaced | Replaced by |
| CPX-551[37] | 1551B | CPX-751 | |
| SDX-551 | 2551HR | SDX-751 | |
| SDX-551TH | 2551THR | FSP-751T | |
| FDX-551[38] | 5551B | FST-751 | |
| FDX-551R | 5551R | FST-751R | |
| CMX-1 | M500C | CMX-2 | |
| CMX-2 | M500CH | CMX-1 | |
| MMX-1[39] | M500MB | ||
| MMX-2 | M502M | ||
| MMX-101 | M501M | ||
| ISO-X | M500X |
| Silent Knight model | System Sensor model | Replaced | Replaced by |
| SK-MONITOR[40] | M500MB | SD500-AIM | Still in production |
| SK-MONITOR-2 | M500DM | None | Still in production |
| SK-MINIMON | M501M | HFS-MM SD500-MIM |
| SK-ZONE | M502M | SD500-SDM | Still in production |
| SK-CONTROL | M500S | SD500-ANM | Still in production |
| SK-RELAY | M500R | HFS-MR SD500-ARM SD505-DUCTR (with SK-DUCT-W) |
| SK-RELAYMON-2 | M500DMR | None | Still in production |
| SK-ISO | M500X | SD500-LIM | Still in production |
- ↑ https://www.freepatentsonline.com/5400203.html
- ↑ "1551B Plug-in Intelligent Ionization Sensors with Communications" (I56-1436-00). System Sensor (1999).
- ↑ "2551HR Plug-in Intelligent Photoelectronic Sensors with Communications" (I56-1437-00). System Sensor (1999).
- ↑ https://www.securityandfire.honeywell.com/notifier/en-us/news/Articles/bright-white-addressable-faceplate-modules
- ↑ "500 Series™ Intelligent Sensors with Integral Communications" (A05-228-01). System Sensor (April 1997).
- ↑ "200 Series Mounting Base Options" (A05-1020-002). System Sensor (April 2006).
- ↑ "M500M-4-20 4-20mA Analog Input Module" (I56-3070-003). System Sensor (March 11, 2016).
- ↑ "M500R Relay Control Module" (I56-3852-004). System Sensor (March 11, 2016).
- ↑ "500 Series™ Intelligent Monitor and Control Modules" (A05-224-01). System Sensor (April 1997).
- ↑ https://tecumsehtech.com/Detectors-and-Modules
- ↑ https://web.archive.org/web/20040219083128/http://www.faradayllc.com/products_addressable.html
- ↑ https://web.archive.org/web/20040401233430/http://faradayfirealarms.com/products_initiating.html
- ↑ "CP300(A) - Addressable Ionization Detector" (DF-51311). Fire-Lite Alarms (February 15, 2001).
- ↑ "4812.pdf". Fire-Lite Alarms.
- ↑ "SD300(A)/SD300T(A) - Addressable Photoelectric Detectors" (DF-51320). Fire-Lite Alarms (February 15, 2001).
- ↑ "MS-9200 Addressable Modules" (DF-51339). Fire-Lite Alarms (February 15, 2001).
- ↑ "ASD-I Analog Ionization Sensor" (9020-0277). Fire Control Instruments (1997).
- ↑ "ASD-P Analog Photoelectronic Sensor" (9020-0275). Fire Control Instruments (1997).
- ↑ "ATD,ATD-R Analog Thermal Sensor" (9020-0278). Fire Control Instruments (1997).
- ↑ https://web.archive.org/web/20041205070305/http://firecontrolinstruments.com/prod-id.html
- ↑ "SCE-SS and RCE-SS Addressable Control and Relay Modules" (CS-2466). Gamewell (October 25, 2004).
- ↑ "PIDP-SS, PID-SS, CZI-SS, and DPID-SS Monitor Modules with SmartScan™" (CS-2465). Gamewell (October 25, 2004).
- ↑ "SS-LI Fault Isolator Module" (CS-2464). Gamewell (October 25, 2004).
- ↑ "Velociti™ Series AMM-2F" (9020-0626). Fire Control Instruments (2005).
- ↑ "Velociti™ Series AMM-2IF" (9020-0629). Fire Control Instruments (2005).
- ↑ "Velociti™ Series AMM-4F" (9020-0624). Fire Control Instruments (2005).
- ↑ "Velociti™ Series AMM-4SF" (9020-0630). Fire Control Instruments (2005).
- ↑ "Velociti™ Series AOM-2RF" (9020-0625). Fire Control Instruments (2005).
- ↑ "Velociti™ Series AOM-2SF" (9020-0627). Fire Control Instruments (2005).
- ↑ "Velociti™ Series AOM-MUXF, AOM-TELF" (9020-0628). Fire Control Instruments (2005).
- ↑ "TC81021000 Releasing Control Module" (9021-60905). Honeywell Gamewell-FCI (November 2017).
- ↑ "Addressable Devices with Intelligent Device Protocol (IDP)" (350361). Silent Knight (2015).
- ↑ "XLS140-2 Intelligent Addressable Fire Alarm Control Panel" (85-3128-13). Honeywell (September 2022).
- ↑ "TC811A1006 FAULT ISOLATOR MODULE FOR FIRE AND SECURITY SYSTEMS" (I56-3630-002). Honeywell (2012).
- ↑ "TC811A1014 FAULT ISOLATOR MODULE" (I56-1136-003). Honeywell (2020).
- ↑ "Monaco Products Catalog". Monaco Enterprises (September 2024).
- ↑ https://firealarms.tv/collection/notifier-cpx-551/
- ↑ https://i.ebayimg.com/images/g/2QYAAOSw12Vl4kZk/s-l1600.jpg
- ↑ "FMM-1(A), FMM-101(A), FZM-1(A) & FDM-1(A) - Monitor Modules with FlashScan®" (DN-6720). Notifier (July 30, 2015).
- ↑ "Addressable Devices with SK Protocol" (53623). Silent Knight (2013).